Forfatter Emne: Alarm "airflow can't be reached"  (Læst 17879 gange)

0 Medlemmer og 2 Gæster læser dette emne.

Offline LucyandJean

  • Begynder
  • *
  • Indlæg: 7
  • Respekt optjent: +0/-0
Alarm "airflow can't be reached"
« Dato: Jan 10, 2023, 05:11 »
Anybody knows what this alarm means and how it can be fixed?

Thanks!

Offline michael f

  • Beta tester
  • Top of the pop
  • *
  • Indlæg: 7634
  • Respekt optjent: +226/-180
  • NBE Support
Sv: Alarm "airflow can't be reached"
« Svar #1 Dato: Jan 10, 2023, 06:17 »
Anybody knows what this alarm means and how it can be fixed?

Thanks!

It may be due to a blockage in the system.
Maybe a plug in a hose.
Maybe a faulty meter.
The quick solution is to switch off the flow measurement and use fan numbers.
Best regards
Michael fra StokerCloud Support http://www.nbe.dk/sadan-fungere-stokercloud/
Find manualer her https://www.nbe.dk/manualer-nbe/
Tekniske vejledninger https://www.nbe.dk/tekniske-vejledninger/

Offline LucyandJean

  • Begynder
  • *
  • Indlæg: 7
  • Respekt optjent: +0/-0
Sv: Alarm "airflow can't be reached"
« Svar #2 Dato: Jan 10, 2023, 12:54 »
Thanks for the answers.

I just have a few follow-up questions: which hoses should I check? The ones bringing air to the combustion chamber (my installer told me it was related to the flue pipes)?

If I switch off the flow measurements, which fan numbers should I use? and is there a risk that the boiler will get damaged?

Thanks a lot!

Offline michael f

  • Beta tester
  • Top of the pop
  • *
  • Indlæg: 7634
  • Respekt optjent: +226/-180
  • NBE Support
Sv: Alarm "airflow can't be reached"
« Svar #3 Dato: Jan 10, 2023, 14:31 »
Thanks for the answers.

I just have a few follow-up questions: which hoses should I check? The ones bringing air to the combustion chamber (my installer told me it was related to the flue pipes)?

If I switch off the flow measurements, which fan numbers should I use? and is there a risk that the boiler will get damaged?

Thanks a lot!

It is the hoses from the fan, up to the print on the burner.

You must adapt the fan numbers to your combustion.
See schedule https://www.nbe.dk/wp-content/uploads/2015/08/Montering-af-blaesere-DK.pdf
A link to your control on StokerCloud or information about the kW size of the boiler will help.

There is no damage to the installation by using blower numbers.
It's just another way to control the combustion.
Best regards
Michael fra StokerCloud Support http://www.nbe.dk/sadan-fungere-stokercloud/
Find manualer her https://www.nbe.dk/manualer-nbe/
Tekniske vejledninger https://www.nbe.dk/tekniske-vejledninger/

Offline michael f

  • Beta tester
  • Top of the pop
  • *
  • Indlæg: 7634
  • Respekt optjent: +226/-180
  • NBE Support
Sv: Alarm "airflow can't be reached"
« Svar #4 Dato: Jan 10, 2023, 15:08 »
Here is the link to our control:
https://stokercloud.dk/v3/#/LucyandJean/main-page

Switch off the alarm, and when the flow control is switched off you are ready for ignition.
Blower numbers are ok  :)
Best regards
Michael fra StokerCloud Support http://www.nbe.dk/sadan-fungere-stokercloud/
Find manualer her https://www.nbe.dk/manualer-nbe/
Tekniske vejledninger https://www.nbe.dk/tekniske-vejledninger/

Offline LucyandJean

  • Begynder
  • *
  • Indlæg: 7
  • Respekt optjent: +0/-0
Sv: Alarm "airflow can't be reached"
« Svar #5 Dato: Jan 10, 2023, 15:37 »
Thanks!!

So the 2 clear hoses on the burner are just for flow measurement?

Offline michael f

  • Beta tester
  • Top of the pop
  • *
  • Indlæg: 7634
  • Respekt optjent: +226/-180
  • NBE Support
Sv: Alarm "airflow can't be reached"
« Svar #6 Dato: Jan 10, 2023, 15:48 »
Thanks!!

So the 2 clear hoses on the burner are just for flow measurement?

Yes  :)
Best regards
Michael fra StokerCloud Support http://www.nbe.dk/sadan-fungere-stokercloud/
Find manualer her https://www.nbe.dk/manualer-nbe/
Tekniske vejledninger https://www.nbe.dk/tekniske-vejledninger/

Offline LucyandJean

  • Begynder
  • *
  • Indlæg: 7
  • Respekt optjent: +0/-0
Sv: Alarm "airflow can't be reached"
« Svar #7 Dato: Jan 11, 2023, 12:50 »
Thanks it worked!

Could you tell me what the benefits of the airflow regulation are over the regulation with fan speed? Is it worth fixing it, and if yes, could you work me through the steps to do it?

Thanks a lot!

Offline michael f

  • Beta tester
  • Top of the pop
  • *
  • Indlæg: 7634
  • Respekt optjent: +226/-180
  • NBE Support
Sv: Alarm "airflow can't be reached"
« Svar #8 Dato: Jan 11, 2023, 13:51 »
Thanks it worked!

Could you tell me what the benefits of the airflow regulation are over the regulation with fan speed? Is it worth fixing it, and if yes, could you work me through the steps to do it?

Thanks a lot!

Air flow regulation is an attempt to measure the air flow and regulate based on the pressure that is measured.
When it works it is very accurate, but several things can interfere with that measurement.
For example, dust in the hoses, a sharp bend on the hose, or a hole in the hose.

Using fan numbers is just as effective.
However, without the possibilities of incorrect adjustment based on incorrect pressure measurements.
Forget the flow regulation, it's not worth the effort.

Best regards
Michael fra StokerCloud Support http://www.nbe.dk/sadan-fungere-stokercloud/
Find manualer her https://www.nbe.dk/manualer-nbe/
Tekniske vejledninger https://www.nbe.dk/tekniske-vejledninger/

Offline Maximus69

  • Begynder
  • *
  • Indlæg: 3
  • Respekt optjent: +0/-0
Sv: Alarm "airflow can't be reached"
« Svar #9 Dato: Nov 22, 2023, 20:59 »
Hello, I'm experiencing the same issue with my RTB10 boiler.
I often get the alarm "air flow can't be reached" after compressor clean cycle.
My only solution is to unplug and clean the 2 transparent hoses on the burner, clear the alarm then restart the controler. It is very unconvenient and I wonder if could use the same solution as LucyandJean, using the fan numbers instead of the air flow measurement.
Coud you please give me advice regarding this case ?

Best regards,

Max

Offline michael f

  • Beta tester
  • Top of the pop
  • *
  • Indlæg: 7634
  • Respekt optjent: +226/-180
  • NBE Support
Sv: Alarm "airflow can't be reached"
« Svar #10 Dato: Nov 22, 2023, 21:06 »
Hello, I'm experiencing the same issue with my RTB10 boiler.
I often get the alarm "air flow can't be reached" after compressor clean cycle.
My only solution is t so unplug and clean the 2 transparent hoses on the burner, clear the alarm then restart the controler. It is very unconvenient and I wonder if could use the same solution as LucyandJean, using the fan numbers instead of the air flow measurement.
Coud you please give me advice regarding this case ?

Best regards,

Max

Use blower numbers  :)


Best regards
Michael fra StokerCloud Support http://www.nbe.dk/sadan-fungere-stokercloud/
Find manualer her https://www.nbe.dk/manualer-nbe/
Tekniske vejledninger https://www.nbe.dk/tekniske-vejledninger/

Offline Maximus69

  • Begynder
  • *
  • Indlæg: 3
  • Respekt optjent: +0/-0
Sv: Alarm "airflow can't be reached"
« Svar #11 Dato: Nov 22, 2023, 21:29 »
Hi Michael and thanks a lot for this very quick answer !  ;D
Could you please confirm the settings I have to modify to do so ?
What I understand/imagine is to set to ON the "use fan RPM alarm" setting and set to OFF the "Airflow regulation" setting of the "FAN" tab. Am I right ?
Thanks a lot.

Max
« Senest Redigeret: Nov 22, 2023, 21:31 af Maximus69 »

Offline michael f

  • Beta tester
  • Top of the pop
  • *
  • Indlæg: 7634
  • Respekt optjent: +226/-180
  • NBE Support
Sv: Alarm "airflow can't be reached"
« Svar #12 Dato: Nov 23, 2023, 05:39 »
Hi Michael and thanks a lot for this very quick answer !  ;D
Could you please confirm the settings I have to modify to do so ?
What I understand/imagine is to set to ON the "use fan RPM alarm" setting and set to OFF the "Airflow regulation" setting of the "FAN" tab. Am I right ?
Thanks a lot.

Max

Dont use air flow regulation.
Dont use rpm regulation.
« Senest Redigeret: Nov 23, 2023, 05:40 af michael f »
Best regards
Michael fra StokerCloud Support http://www.nbe.dk/sadan-fungere-stokercloud/
Find manualer her https://www.nbe.dk/manualer-nbe/
Tekniske vejledninger https://www.nbe.dk/tekniske-vejledninger/

Offline Maximus69

  • Begynder
  • *
  • Indlæg: 3
  • Respekt optjent: +0/-0
Sv: Alarm "airflow can't be reached"
« Svar #13 Dato: Nov 23, 2023, 17:42 »
Thanks for your help, I will try this solution after next air flow regulation breakdown.

Best regards

Max