Forfatter Emne: HELP NEEDED FOR SCOTTE BURNER 24KW  (Læst 7588 gange)

0 Medlemmer og 1 Gæst læser dette emne.

Offline didier

  • Øvet
  • **
  • Indlæg: 28
  • Respekt optjent: +0/-0
HELP NEEDED FOR SCOTTE BURNER 24KW
« Dato: Dec 15, 2009, 08:11 »
I have a recently installed scotte burner 24kw and woody boiler 30kw. (6months old)
It ran fine for a couple of months but the past months it is having trouble.
Every 2 day's i have to empty the ashtray cause of plenty with black burned pellets !!! :'(
The installation guy tried out everything, changed out everything but can't get it running properly again.
Everything is cleaned, chimney allso, nothing helps me out.
I do not have a good instruction manual, i would like to get one to check all the menu's.
Is there anyone out here who could help me out please.

I am spoiling pellets like hell, i am using 65 bags from 15kg in 20days !!
I can't read or write danish so please try to help me out in english.
any help is welcome, thanks a lot.

Offline skipper

  • Begynder
  • *
  • Indlæg: 1
  • Respekt optjent: +0/-0
Sv: HELP NEEDED FOR SCOTTE BURNER 24KW
« Svar #1 Dato: Dec 15, 2009, 08:41 »
Jeg ved desværre intet om Scotte, men har et bio 18 fyr. Er det ikke for sådan en som mig, dvs. er det ogsåfor Bio 18 brugere?
Hilsen og tak

Offline MHES

  • Beta tester
  • Top of the pop
  • *
  • Indlæg: 7386
  • Respekt optjent: +472/-56
  • Der findes ikke dumme spørgsmål - kun dumme svar
    • MHES
Sv: HELP NEEDED FOR SCOTTE BURNER 24KW
« Svar #2 Dato: Dec 15, 2009, 08:46 »
Hi,

Black, not fully burned pellets, normally is a sign of too much air-flow through the burner.
This results in the pellets "flying" with the airstream, before they are fully burned to ashes.
Typically this is again a result of too high drag in the chimney, caused of missing drag-regulator (drag-reducer) in the chimney.
When the wether get colder, the temperature difference between top and buttom of chimney increses, and the drag as well.
The air-flow through the burner is af som of the airstream from the blower and the drag from the chimney.
Therefor - first make sure that you have a controlled low drag from the chimney, thereafter adjust the air-stream (blower) to correct setpoint.
These adjustments are fundamental for the adjustment of the system, and should be done by the installer.

Best regards
Michael

I have a recently installed scotte burner 24kw and woody boiler 30kw. (6months old)
It ran fine for a couple of months but the past months it is having trouble.
Every 2 day's i have to empty the ashtray cause of plenty with black burned pellets !!! :'(
The installation guy tried out everything, changed out everything but can't get it running properly again.
Everything is cleaned, chimney allso, nothing helps me out.
I do not have a good instruction manual, i would like to get one to check all the menu's.
Is there anyone out here who could help me out please.

I am spoiling pellets like hell, i am using 65 bags from 15kg in 20days !!
I can't read or write danish so please try to help me out in english.
any help is welcome, thanks a lot.

Styring nr. 47387 RTB på Android tablet
Opvarmer ca. 270 m2
RTB 10 kW v13.xxxx med VVB-styring og udvidelsesprint.
Årsforbrug 4,5 - 5 ton.
Online fra fyr https://stokercloud.dk/v3/#/mhes_rtb10/main-page
Hjemmeside www.mhes.dk
"How to do" videoer http://mhes.dk/hjem-2/videoer.html

Offline Frank_rasmussen

  • Top of the pop
  • *****
  • Indlæg: 759
  • Respekt optjent: +23/-31
Sv: HELP NEEDED FOR SCOTTE BURNER 24KW
« Svar #3 Dato: Dec 15, 2009, 11:16 »
Jeg ved desværre intet om Scotte, men har et bio 18 fyr. Er det ikke for sådan en som mig, dvs. er det ogsåfor Bio 18 brugere?
Hilsen og tak
This is not the place for you. Go to e.g. http://www.stokerpro.dk/viewforum.php?f=135
Woody 10 kW (høj sort/rød kedel) (v. 6.85)
140 kvm hus fra 1914 med 1. sal fra 80'erne
Iltstyring, VVB-prioritering og kompressor rens
160 l Metro vandvarmer med elpatron

Offline didier

  • Øvet
  • **
  • Indlæg: 28
  • Respekt optjent: +0/-0
Sv: HELP NEEDED FOR SCOTTE BURNER 24KW
« Svar #4 Dato: Dec 15, 2009, 21:51 »
hello michael, you could be wright with the chimney draught, i am at the moment trying to make better settings trough the manufacturer, if we don't reach the good settings i will have to investigate the chimneydraught, i also think it is to high as you mention.

To frank sorry but i did not know this is not the good forum, i tried to find some help.

anyway thanks a lot to everybody.

Offline Paw

  • Top of the pop
  • *****
  • Indlæg: 1210
  • Respekt optjent: +36/-6
Sv: HELP NEEDED FOR SCOTTE BURNER 24KW
« Svar #5 Dato: Dec 16, 2009, 08:04 »
hello didier, this is the good forum, it was skipper Frank refered too
MVH Paw
Intet er umuligt, det tager bare lidt længere tid.

Service videoer fra NBE
https://mhes.dk/hjem-2/videoer

Læs her
http://www.mhes.dk/

Mit fyr online
http://pillefyr.nordjysk-bioenergi.dk/dev/showmain.php?&mac=pawerwoody

Offline Frank_rasmussen

  • Top of the pop
  • *****
  • Indlæg: 759
  • Respekt optjent: +23/-31
Sv: HELP NEEDED FOR SCOTTE BURNER 24KW
« Svar #6 Dato: Dec 16, 2009, 09:34 »
Yes, I was refering to a danish Bio18-user that for some reason wrote in this tread. Very sorry about the misunderstanding.

I hope you are still with us...
« Senest Redigeret: Dec 16, 2009, 09:49 af Frank_rasmussen »
Woody 10 kW (høj sort/rød kedel) (v. 6.85)
140 kvm hus fra 1914 med 1. sal fra 80'erne
Iltstyring, VVB-prioritering og kompressor rens
160 l Metro vandvarmer med elpatron

Offline didier

  • Øvet
  • **
  • Indlæg: 28
  • Respekt optjent: +0/-0
Sv: HELP NEEDED FOR SCOTTE BURNER 24KW
« Svar #7 Dato: Dec 16, 2009, 22:38 »
Hello, ok, sorry for the misunderstanding. ;D

First off all thanks to Frank,
this morning I checked the draft stabiliser in the chimney....
IT WAS LOCKED FOR SOME REASON  >:(
That way it could not work anyhow, who has done this, i don't know at all but i will keep an eye on this in the near future.

My black pellets problem started since a few weeks ago it started getting cold over here in Belgium.
The installation guy came over, cleaned everything and changed a lot off parts, shortly a long story to explain.
After all of that it did NOT became any better untill i called the manufacturer NBE in Denmark and had Jannich Hansen on the phone.
Very nice person and very helpfull, great service and they know what they are talking about.
Since yesterday he started checking my complete settings in the controller of the scotte burner.
I must admit that there was a lot of settings wrong in the menu's... :( thanks to my installation guy / salesmen.

Today we checked again after mentioning to him the DRAFT REGULATOR was closed and locked....so we did change some more settings this morning and guess what  ;D  ;D  ;D

Yess, everything seems to be allright at this moment, my ashtray is a lot less full then before and the ashes are as normal as before when it was brandnew.
Finally we are happy SCOTTE USERS again.

MANY MANY THANKS to the manufacturer for helping me out and offcourse allso to this forum and the users for giving me the tips.
Have a nice and WARM winter.
 ;)
« Senest Redigeret: Dec 16, 2009, 22:42 af didier »